UH Disconnect Switch Size

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Have a 2p-20a breaker(2#12’s) feeding a 100a disconnect fora unit heater. The unit heater is about 2 Kw. How/why could there be a 100adisconnect? Thanks.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
It's overkill, but not an issue. The disconnect has to be rated to handle the current that will be sent through it. So it will see under 10 amps and has the ability to handle ten times that. Someone spent too much money on that disconnect. But there is no safety hazard and no code violation.
 

mstrlucky74

Senior Member
Location
NJ
So the disconnect serves as a manual means of disconnect only....not for fault, short circuit etc.?

Sent from my SM-G955U using Tapatalk
 
Status
Not open for further replies.
Top