milwaukeesteve
Senior Member
- Location
- Milwaukee, WI
Re: uh oh, another SA question
If the outlets are installed 'in accordance with', such as your plug mold example, than 210.52(B) states that they must be 20A SA outlets, because in the code rule it states 'in accordance with'.
It really is that simple.
If the outlet is part of (C) than it is part of (B). If it is part of (B), then it is a SA circuit and receptacle.
There is no other way around it. The language states it right in those to sections.
No exception is going to save you now.
No other code rule can touch it (i.e. 422.16).
If the outlets are installed 'in accordance with', such as your plug mold example, than 210.52(B) states that they must be 20A SA outlets, because in the code rule it states 'in accordance with'.
It really is that simple.
If the outlet is part of (C) than it is part of (B). If it is part of (B), then it is a SA circuit and receptacle.
There is no other way around it. The language states it right in those to sections.
No exception is going to save you now.
No other code rule can touch it (i.e. 422.16).