UL 1424 and FPL Cable

Status
Not open for further replies.

vw55

Member
Location
California
My understanding is that type FPL cable can be run above 7' in free air as long as it's properly supported. If it's in a plenum space, it must be FPLP cable.

The scope of UL 1424, (available on line at http://ulstandardsinfonet.ul.com/scopes/1424.html) paragraph 1.7 specifically states: "As noted in 1.8, "Power-limited fire-alarm circuit cable" is used with protection such as raceway.

Paragraph 1.8 specifically states: "Power-limited fire-alarm circuit cable" is used: a) In nonconcealed spaces in which the exposed length of cable does not exceed 10 ft. or 3.05m, and b) In raceway.

My question is whether or not UL 1424 implements a requirement to install power-limited fire-alarm circuit cable, types FPL and FPLR, occurring above a ceiling in conduit?
 