don_resqcapt19 said:
The issue is the fact that a series arc is self extinguishing at the zero crossing(at dwelling unit voltages) and a single arc of less than a 1/2 cycle will never have enough energy to cause any type of of problem on a 120 volt circuit. What is commonly called a series arc is really a high resistance connection that produces excessive heat when current flows. It really isn't an arc as there is a physical connection, maybe of very high resistance, but still a physical connection. An arc is current flow between two points without a physical connection.
Don
I am a little confused now. Are you implying that there should be no need to detect series arcs in 120V circuits?
Here is a link that talks about the potential for fires in series arcs:
http://www.iaei.org/subscriber/magazine/00_e/mcmanus.htm
(see 58.1.3)
I would think that lots of parallel arcs could also be self extinquishing each 1/2 cycle.
One issue could be when the connection is constantly or intermittently opening and closing. Thus constantly re-establishing the arc.
I could see a large potential for problems in a series arc of a highly inductive or capacitive load that has a large inrush current when first turned on. If this load were intermittently being interrupted (in a series fashion) there could be large currents flowing and lots of energy.
John said:
Dear John,
Thank you for using the Schneider Electric web site. There are some models of vacuum cleaners that have problems with AFI circuits. Most are 2-speed models that are started out in high speed. We have found that starting in low speed does not trip the breaker. On single speed vacuums start out the vacuum in high carpet setting to eliminate startup surge.
Please feel free to contact us if we can assist you further.
Thank you,
Tim xxxxxxx
Product Support Specialist
This is exactly the text I read before. Isn't intersting that inrush current appears to be the cause of the tripping?
I have done lots of testing on inrush currents and viewed a lot those waveforms. They are usually pretty "clean" and continuously decaying in amplitude. They usually only last for a few cycles. Not like I would expect an arcing fault to look.
I would think that a very well done software routine could tell the difference.
But I also think it is not trivial at all and they probably need to spend a lot more time and money on more sophisticated devices to be able to differentiate between normal events and true arcing faults. Especially series arcs.