Jesse Livingston
Member
- Location
- Grand Cayman
Looking for some help on this one. We have specified a fixture with a UL 1838 listing to be installed within 5' of the pool edge. 680.23 (A) (6) would appear to allow this as long as the power supply is listed for swimming pool use. The inspector is arguing that it needs to be UL 676 listed, however; this listing refers specifically to "underwater fixtures" and the code only refers to "listed low-voltage fixtures".
The inspector has also argued that 680.26 (7) requires all "fixed metal parts" to be bonded, however; I do not think a "light fixture", is a "fixed metal part". While the fixture is metal, 680.23 (A) (6) states "not requiring grounding".
Love for some opinions on this one. Thanks in advance.


The inspector has also argued that 680.26 (7) requires all "fixed metal parts" to be bonded, however; I do not think a "light fixture", is a "fixed metal part". While the fixture is metal, 680.23 (A) (6) states "not requiring grounding".
Love for some opinions on this one. Thanks in advance.