I understand why the requirement for the UL508 certification. As an general construction inspector I need to know if a control panel / enclosure is UL508 compliant
Within the 2005 Article 409 and UL508A a nameplate that states:
(1) Manufacturer's name, trademark, or other descriptive marking by which the organization responsible for the product can be identified.
(2) Supply voltage, phase, frequency, and full-load current.
(3) Short-circuit current rating of the industrial control panel based on one of the following:
a. Short-circuit current rating of a listed and labeled assembly
b. Short-circuit current rating established utilizing an approved method
FPN: UL 508A-September 2005, Supplement SB, is an example of an approved method.
(4) If the industrial control panel is intended as service equipment, it shall be marked to identify it as being suitable for use as service equipment.
(5) Electrical wiring diagram or the number of the index to the electrical drawings showing the electrical wiring diagram.
(6) An enclosure type number shall be marked on the industrial control panel enclosure.
Then it is up to you IMO to ensure that the Available Fault Current does not exceed the SCCR rating of the panel, if you are the AHJ (authority of having juristiction).
Just my $.02