I have a resistive heating load of 200 A and a panel that will have a disconnect and/or OCPD, a contactor, and a control circuit (not important in this discussion). The plan was to have the disconnect and branch circuit protection be the same device, however it appears if I do that then it would have to be sized at 125% of the FLA, whereas if the disconnect and OCPD are separate (and the OCPD is a fuse) than both components can be sized based on 100% FLA. The relevant sections are:
A related question: UL 508A doesn't seem to distinguish between continuous and non-continuous load, except for the Exception to 30.2.1 which says the 125% sizing isn't required if the MCCB is rated at 100% load, however the NEC at least allows a maximum time at FLA to be considered continuous. Am I missing something there?
- 31.6.3, which states the branch circuit protection shall be sized based on the ampacity of the field wiring, which leads to
- 28.3.8, which states the field wiring ampacity shall be 100% of the FLA
- 29.6.1 likewise states internal wiring shall be sized to the FLA of the load
- 30.2.2(a)(1) states a non-fused switch for a non-motor load shall be sized at 100% FLA
A related question: UL 508A doesn't seem to distinguish between continuous and non-continuous load, except for the Exception to 30.2.1 which says the 125% sizing isn't required if the MCCB is rated at 100% load, however the NEC at least allows a maximum time at FLA to be considered continuous. Am I missing something there?