David Charles
Member
- Location
- Kansas City
- Occupation
- EE
I wanted to make sure i had this correct.
what is the maximum branch circuit protection allowed for both the primary and secondary sides of a 1500 VA 480/120 volt single-phase power transformer.
Primary:
1500/480 = 3.125
using table 35.2 in UL 508A standard
3.125 * 2.5 = 7.8125
Secondary:
1500/120 = 12.5
12.5*1.25 = 15.625
so the answer would be Primary = 8amp, and secondary = 20amp.
what is the maximum branch circuit protection allowed for both the primary and secondary sides of a 1500 VA 480/120 volt single-phase power transformer.
Primary:
1500/480 = 3.125
using table 35.2 in UL 508A standard
3.125 * 2.5 = 7.8125
Secondary:
1500/120 = 12.5
12.5*1.25 = 15.625
so the answer would be Primary = 8amp, and secondary = 20amp.