SB4.2 Exception No. 3 states that "Enclosure air conditionors or multimotor and combination load equipment that is cord and attachment plug conneced OR SUPPLIED FROM A BRANCH CIRCUIT PROTECTED AT 60A OR LESS is not required to have a short circuit current rating.
If I have process equipment, for example an industrial fluid filling machine like brake fluid or radiator fluid, and the main OCPD that is on the control panel is less than 60A, then I do not have to supply the SCCR rating for the machine? It does not need any further analysis than the main panel OCPD is less than 60A?
If I have process equipment, for example an industrial fluid filling machine like brake fluid or radiator fluid, and the main OCPD that is on the control panel is less than 60A, then I do not have to supply the SCCR rating for the machine? It does not need any further analysis than the main panel OCPD is less than 60A?