Hello,
I am sizing a feeder circuit for a panel according to UL 508A and came into a question:
My input current is of 76.5 A (considering all the loads), thus, it is fine for me to use a cable of 4 AWG (max. 85A @ 75 c).
For the circuit breaker I did 76.5 A x 1.25 = 96 A and then I selected a breaker of 100A.
My question is:
Is it ok for me to keep this configuration according to UL 508A? 100A breaker + 4 AWG load side cable
Or do I need to level up the cables?
Thank you very much in advance!