There is a line in the Supplement SA for UL 508A panels, "1.1 Exception No. 2 c)".
I am working on a design for a panel in an ordinary location where the customer specified a Rockwell IO board that is listed under a hazardous location standard.
Class I, Division 2, Group A, B, C and D
The part number in question is 1492-AIFM8-F-5.
This section of the standard makes it clear to me a component listed for a hazardous location with intrinsically safe input/output connections like an IO field wiring board can't be used in an oridinary panel. I'm struggling to fine the reasoning for this, or if I'm misunderstanding this section of the supplement. Has anyone run across this before on a UL 508A panel?
Exception No. 2: The following hazardous locations equipment and associated apparatus shall not be used as part of an ordinary locations industrial control panel:
a) An explosion-proof enclosure marked for Class I hazardous locations (or Type 7).
b) A dust-ignition-proof enclosure marked for Class II hazardous locations (or Type 9),
c) A barrier or other equipment that provides intrinsically safe input/output connections for use in Class I, II, and III hazardous locations
I am working on a design for a panel in an ordinary location where the customer specified a Rockwell IO board that is listed under a hazardous location standard.
Class I, Division 2, Group A, B, C and D
The part number in question is 1492-AIFM8-F-5.
This section of the standard makes it clear to me a component listed for a hazardous location with intrinsically safe input/output connections like an IO field wiring board can't be used in an oridinary panel. I'm struggling to fine the reasoning for this, or if I'm misunderstanding this section of the supplement. Has anyone run across this before on a UL 508A panel?