AJElectric
Member
- Location
- Iowa
- Occupation
- Electrical Contractor, instrumentation and controls integration
New to 508a here in our shop. I know how to do basic load calculations, but I'm wondering if there are any requirements by UL for sizing these components for control wiring.
Control Transformer - I can't find any sizing requirements (only circuit conductor sizing, bonding, and OCP requirements)
As an example, currently working on a project where the sum of all 120VAC loads is about 850W; plus two devices nameplate 3.0A (but in reality they're just a timer & solenoids total 50W max); plus a 120V convenience outlet with 3A OCP.
The loads are all controlled by a PLC and would never all operate at the same time. The max would be maybe 500W. I intend to use a 750VA transformer with 8A MEN fuse on the secondary, and 14AWG conductors on all secondary circuits. Would this meet UL 508A standards?
Power supplies - 42.2.3 max 50% load unless it meets UL61010 etc. and then 42.2.3.2 sizing the overcurrent protection. This is all pretty clear that if the sum of all loads is above P.S. rating then you need OCP. Sounds like it would be OK to have qty. 50 of 10-watt relays and indicator lights on a 120W power supply, as long as there is proper OCP on the circuit(s).
A similar but separate question - 49.2 wording "sum of all current ratings...that are able to be operated simultaneously..." does this mean mechanically interlocked to prevent running at the same time? Or hard-wired relay logic? Or is PLC control adequate?
Control Transformer - I can't find any sizing requirements (only circuit conductor sizing, bonding, and OCP requirements)
As an example, currently working on a project where the sum of all 120VAC loads is about 850W; plus two devices nameplate 3.0A (but in reality they're just a timer & solenoids total 50W max); plus a 120V convenience outlet with 3A OCP.
The loads are all controlled by a PLC and would never all operate at the same time. The max would be maybe 500W. I intend to use a 750VA transformer with 8A MEN fuse on the secondary, and 14AWG conductors on all secondary circuits. Would this meet UL 508A standards?
Power supplies - 42.2.3 max 50% load unless it meets UL61010 etc. and then 42.2.3.2 sizing the overcurrent protection. This is all pretty clear that if the sum of all loads is above P.S. rating then you need OCP. Sounds like it would be OK to have qty. 50 of 10-watt relays and indicator lights on a 120W power supply, as long as there is proper OCP on the circuit(s).
A similar but separate question - 49.2 wording "sum of all current ratings...that are able to be operated simultaneously..." does this mean mechanically interlocked to prevent running at the same time? Or hard-wired relay logic? Or is PLC control adequate?