Do straps for emt rmc romex mc uf ECT. have to be ul approved ?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Do straps for emt rmc romex mc uf ECT. have to be ul approved ?

UL does not "approve" anything. Only the AHJ can approve the use of something.

UL does list or recognize products and this will often lead a AHJ to approve its use.

If by straps you mean the single hole nail on clips my guess is that they are part of the conduit system and thus have to be listed.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Yes, UL does list conduit straps, and generally the UL bug is stamped or pressed into the strap so as to be easily visible after installation. So technically if you are in an area where NRTL listing is required, an AHJ could red tag an installation in which someone used unlisted straps or where for some reason the UL listing mark is hidden from view.
 