UL listing requirement for added control

Status
Not open for further replies.

yha3

Member
I have and inspector asking a correction for a field install added stop start station that was put togheter with Ul listed box and a UL listed button. What does the NEC say about this? I can't find anything.
 

charlie

Senior Member
Location
Indianapolis
Re: UL listing requirement for added control

It is not an NEC issue, it is a UL issue. They tested and listed everything as a complete unit. If you have changed the configuration and added parts, it has to be retested unless it was designed for the added component or modification.

For instance, you install a panelboard and then install circuit breakers that were listed with that panelboard, you have no problem. However, if you install a panelboard and then install circuit breakers that were not listed for use with that panelboard, you have a big problem.

The same would apply if you modified the bus to accept one-half size circuit breakers; the equipment was not tested for use in that manner.

Bottom line, is the box listed for use with the stop button? A call to UL may be in order. :)
 