Is there a publication that explains how much a ul listed product can be changed and not violate the listing?

I can add breakers to a loadcenter - can I change the lugs, add fingers, tap the buss?

The second question is just an example, please answer the first question.
 

bphgravity

Senior Member
Location
Florida
Re: ul listing violated ??

The refrence book for UL listings is the UL directory "green book". The AHJ is the only person that will be able to determine and give special permission if a change is still in compliance with the listing
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: ul listing violated ??

If you are installing an accessory provided by the equipment manufacturer or making a modification in accordance with the manufacturer's instructions, the listing will not be violated. Any other changes may violate the listing.