H hhsting Senior Member Location Glen bunie, md, us Occupation Junior plan reviewer Nov 3, 2020 #1 Does UL 891 listing indicate that switchboard has main bonding jumper or it’s just listing for switchboards no main bonding jumper?
Does UL 891 listing indicate that switchboard has main bonding jumper or it’s just listing for switchboards no main bonding jumper?
petersonra Senior Member Location Northern illinois Occupation engineer Nov 3, 2020 #2 hhsting said: Does UL 891 listing indicate that switchboard has main bonding jumper or it’s just listing for switchboards no main bonding jumper? Click to expand... I think they can be made either way. just like UL Listed MCCs and UL508a listed control panels.
hhsting said: Does UL 891 listing indicate that switchboard has main bonding jumper or it’s just listing for switchboards no main bonding jumper? Click to expand... I think they can be made either way. just like UL Listed MCCs and UL508a listed control panels.
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Nov 3, 2020 #3 Equipment with a removable main bonding jumper would be listed and labeled as Suitable for Use as Service Entrance (SUSE). Equipment with a non-removable main bonding jumper would be listed and labeled as Suitable for Use Only as Service Entrance.
Equipment with a removable main bonding jumper would be listed and labeled as Suitable for Use as Service Entrance (SUSE). Equipment with a non-removable main bonding jumper would be listed and labeled as Suitable for Use Only as Service Entrance.