wmthompson90
Member
- Location
- ky
- Occupation
- electrician
so a UL inspection of the complete unit is not satisfactory? don't they have to be recognized in order to be able to legally place the inspection sticker on there?It appears to not have an NRTL label as a complete asembly
The yellow label says it was inspected by an non-NRTL.
The manufacturer's label only applies to the metal box, when it left the factory.
There has been no UL inspection of the completed assembly.so a UL inspection of the complete unit is not satisfactory? don't they have to be recognized in order to be able to legally place the inspection sticker on there?
so this should not pass inspection?There has been no UL inspection of the completed assembly.
The yellow label simply says 'In my opinion this was built properly'.
Only if unlisted control panels are permitted.so this should not pass inspection?
No, the yellow label only references the SCE labelso this should not pass inspection?
I take the yellow label as saying, the final controls/assembly has been reviewed, by a PE but not an NRTL, for compliance with the Supplement to UL508A and as such should be good for an SCCR of 65kA.No, the yellow label only references the SCE label
That would the the first time I have seen a PE assume that risk. He must do it a lot, because he had stickers printed up.I take the yellow label as saying, the final controls/assembly has been reviewed, by a PE but not an NRTL, for compliance with the Supplement to UL508A and as such should be good for an SCCR of 65kA.
Probably because the vast majority of people buying control panels don't give a rats ass if it has a ul sticker on it and won't pay the extra costs to get it.That would the the first time I have seen a PE assume that risk. He must do it a lot, because he had stickers printed up.
So it satisfies the SCCR requirement, but not the NRTL listing one. Why take that extra step if you are the panel builder? Why not just apply to get UL508a?
I have done this for some 'in house' panels for some large cusfomers.That would the the first time I have seen a PE assume that risk.