I have discovered the following:
A humidifier controller which is supplied by 3 ph 480 has the supply voltage connected to the 3 pole contactor at the T1-T2-T3 terminals and the load is connected to the L1-L2-L3 side of the contactor. Does this violate NEC 110.3 or any other standard. I as a troubleshooter could find this an unsafe condition. The equipment does have a UL label attached which is the suppliers "out".
Comments?
Thanks,
John
A humidifier controller which is supplied by 3 ph 480 has the supply voltage connected to the 3 pole contactor at the T1-T2-T3 terminals and the load is connected to the L1-L2-L3 side of the contactor. Does this violate NEC 110.3 or any other standard. I as a troubleshooter could find this an unsafe condition. The equipment does have a UL label attached which is the suppliers "out".