DanielRodriguez
Member
- Location
- North Carolina
- Occupation
- Automation Engineer
We had a UL inspection recently that caused some confusion regarding the 42.1.3 standard and table 42.2. The situation was as follows.
480VAC Primary, 120VAC secondary, 1KVA single phase control transformer.
Per table 42.2 and units of measurement standard 5.2 the calculations would be as follows.
Primary:
1000 / 480 = 2.083
2.083 * 2.5 = 5.2 (Round Down) = 5A primary CB
Secondary:
1000 / 120 = 8.33
8.33 * 1.67 = 13.91 (Round Up) = 14A Secondary CB
I understood these values to be the maximum sized Protection we could use as implied by the lack of note "a" on the calculations in the table and standard 42.1.3.2. However, The UL inspector said we should be using a 6A Primary CB and a 15A secondary CB? Am I misunderstanding something here, this doesn't seem to match up with the standard.
480VAC Primary, 120VAC secondary, 1KVA single phase control transformer.
Per table 42.2 and units of measurement standard 5.2 the calculations would be as follows.
Primary:
1000 / 480 = 2.083
2.083 * 2.5 = 5.2 (Round Down) = 5A primary CB
Secondary:
1000 / 120 = 8.33
8.33 * 1.67 = 13.91 (Round Up) = 14A Secondary CB
I understood these values to be the maximum sized Protection we could use as implied by the lack of note "a" on the calculations in the table and standard 42.1.3.2. However, The UL inspector said we should be using a 6A Primary CB and a 15A secondary CB? Am I misunderstanding something here, this doesn't seem to match up with the standard.