In many of the “How to calculate SCCR” or “How to raise a panels SCCR” videos that I have watched recently on YouTube it seems as if one of the common sticking points for a panel having a low SCCR is the distribution block that’s usually located after the load side of the main disconnect in the feeder circuit.
If you only have say 2-3 branch circuits and each branch is protected by a set of fuses in a fuse holder, say Class CC for this hypothetical scenario. I don’t seem to see anything in the UL literature stating that you are unable to just wire from the load side of the main disconnect in the feeder, to the line side of the fuse block for branch circuit A and then loop from the line side of fuse block A to the line side of the fuse block for branch circuit B and then from B to C.
Panel cleanliness aside, is there something that I am missing where that would not be acceptable under UL508A?
If you only have say 2-3 branch circuits and each branch is protected by a set of fuses in a fuse holder, say Class CC for this hypothetical scenario. I don’t seem to see anything in the UL literature stating that you are unable to just wire from the load side of the main disconnect in the feeder, to the line side of the fuse block for branch circuit A and then loop from the line side of fuse block A to the line side of the fuse block for branch circuit B and then from B to C.