Good afternoon,
I work for a electrical equipment manufacturer, and every once in a while we get a UL508A control panel. This particular one is a simple one, just a mechanically held lighting contactor (ASCO 918 with 3 wire control) and a switch for it. I need to label the FLA as per UL 508A 49.2 and...I get almost nothing. So I say it's 1A. The coil only draws when switching states, but the 3-wire control pulls 2VA I guess.
My boss, however, is of the opinion that I should include the lighting loads that are controlled by the contactor in this calculation. It's a 6P 30A contactor, so there could be (6) 30A lighting loads going through it, and we have terminal blocks in there so the contractor can easily enter and exit. What's the right thing to say on the nameplate? 1A? 30A? 180A? 5A (the fuse size)?
I work for a electrical equipment manufacturer, and every once in a while we get a UL508A control panel. This particular one is a simple one, just a mechanically held lighting contactor (ASCO 918 with 3 wire control) and a switch for it. I need to label the FLA as per UL 508A 49.2 and...I get almost nothing. So I say it's 1A. The coil only draws when switching states, but the 3-wire control pulls 2VA I guess.
My boss, however, is of the opinion that I should include the lighting loads that are controlled by the contactor in this calculation. It's a 6P 30A contactor, so there could be (6) 30A lighting loads going through it, and we have terminal blocks in there so the contractor can easily enter and exit. What's the right thing to say on the nameplate? 1A? 30A? 180A? 5A (the fuse size)?