bclevasseur
New member
- Location
- Detroit, Michigan
Section 49.2 reads that at a minimum, the FLA marking include the sum of the ampere ratings of all loads that are able to be operated simultaneously plus the primary ampere rating of all control transformers connected to the input voltage. So, do power supplies (and their loads) counts as loads or as control transformers?
To be more specific, the enclosure in question is part of a large material handling system. Due to some of the distances involved, some of the Ethernet connections must be run from the main IT room as fiber and then converted to copper at the location of the PCs. The customer wants all enclosures to be UL 508A listed. Inside these small 120VAC single phase enclosure is just a DC power supply that provides power to the Ethernet fiber/copper converter. Both the power supply and converter are UL listed components. The converter requires 95mA @ 24VDC. The power supply however is rated at 1.4A at 120VAC.
What is the correct 508A FLA rating for this enclosure, 0.02A (the FLA power needed by the converter) or 1.4A (the rating of the DC power supply)?
The real issue then extends to the NEC. If the answer is 1.4A, we are being told that the power to these boxes must be sized to supply the LISTED FLA not what the load really needs. If we have 20 of these boxes, then multiple dedicated 15A circuits would be required to supply the 0.4A these boxes are going to actually use. This is then further exacerbated by the power for the PCs, which have 150W power supplies, but as configured only use 50W (these are custom PCs set-up to be used only to control/monitor the equipment).
To be more specific, the enclosure in question is part of a large material handling system. Due to some of the distances involved, some of the Ethernet connections must be run from the main IT room as fiber and then converted to copper at the location of the PCs. The customer wants all enclosures to be UL 508A listed. Inside these small 120VAC single phase enclosure is just a DC power supply that provides power to the Ethernet fiber/copper converter. Both the power supply and converter are UL listed components. The converter requires 95mA @ 24VDC. The power supply however is rated at 1.4A at 120VAC.
What is the correct 508A FLA rating for this enclosure, 0.02A (the FLA power needed by the converter) or 1.4A (the rating of the DC power supply)?
The real issue then extends to the NEC. If the answer is 1.4A, we are being told that the power to these boxes must be sized to supply the LISTED FLA not what the load really needs. If we have 20 of these boxes, then multiple dedicated 15A circuits would be required to supply the 0.4A these boxes are going to actually use. This is then further exacerbated by the power for the PCs, which have 150W power supplies, but as configured only use 50W (these are custom PCs set-up to be used only to control/monitor the equipment).