I am unaware of any code stating the grounding electrode conductor cannot be paralleled. In a 400 amp service with 2 -200 amp discos we are allowed to run 2-#4's to the electrode(s). I am unaware of what UL 508A is stating.
I would still assume the same rules apply as to CCCs, i.e. not smaller than 1/0.
There is no section which says you can parallel a GEC using smaller conductors. So you want to parallel 'em. Okay... each has to be the required minimum size.That section does not refer to grounding electrode conductor's
There is no section which says you can parallel a GEC using smaller conductors. So you want to parallel 'em. Okay... each has to be the required minimum size.
C) Continuous. Except as provided in 250.30(A)(5) and
(A)(6), 250.30(B)(1), and 250.68(C), grounding electrode
conductor(s) shall be installed in one continuous length
without a splice or joint. If necessary, splices or connections
shall be made as permitted in (1) through (4):
(1) Splicing of the wire-type grounding electrode conductor
shall be permitted only by irreversible compression type
connectors listed as grounding and bonding equipment
or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected
together to form a grounding electrode conductor.
(3) Bolted, riveted, or welded connections of structural
metal frames of buildings or structures.
(4) Threaded, welded, brazed, soldered or bolted-flange
connections of metal water piping.
I thought the code was permissive---if it does say you can't then you can....you all are changing the rules....LOL
While staying permissive, you cannot violate the minimum size GEC requirement. Code offers no avenue to determine a parallel smaller equivalent, such as using fractional ampacity for parallel circuit conductors.Tell me this. I can run a smaller conductor for 2- 200 amp panels to each disconnect and be compliant. Can I run those separate grounding electrode conductor's (#4's) to the same meter instead of the disconnect? If I can run it to the disconnect why can't I run it to the meter instead? Seems no different than a parallel grounding electrode conductor.
I have never done it but I can't seem to find where it may be non compliant..
Connecting two GEC's at the meter for two 200A panels would be a violation because each GEC is not sized for the largest ungrounded conductor where it is connected.
It is what it is. You should know as well as anyone that requirements do not always exhibit logical conclusions. That said, I know you know the process to get it changed.And connect it the panel 4" away from the meter and it is compliant. :?