SteveBB
Member
- Location
- United States
I have a panel being built for a project I'm working on, I'm in the role of electrical project engineer, but I have a background in controls, although I've not ever worked for a UL certified shop I have typically designed to UL508A standards and I haven't had an issues when I've kicked my designs out to a UL certified panel shop to build.
The equipment is coming from an international supplier and I'm not convinced they have calculated the panel nameplate FLA correctly, and before I put in a feeder servicing it I want to feel more comfortable.
My particular question revolves around motors that are controlled from a drive (VFD or Servo Amplifier) and whether or not to use the motor FLA or the drive's input current.
From searches on this board, it seems to be somewhat of a split opinion with regards to this for protection and feeder sizing, my concern is strictly regarding FLA calculation.
A) The supplier has provided an panel nameplate FLA that uses the servo motor FLA as a basis
B) The supplier has provided branch protection per the drive's current input values
I'm ok with B above, it's A that I have pause.
They contend that when the servo motor is detected by the servo drive that the drive automatically limits current, which in a base sense is true, except that I've personally been involved with servo applications where mechanical design wasn't great and given the dynamics of a servo, it's amplifier, it's tune, that a servo motor can easily be driven beyond it's nominal rating and in fact it's built to do just that so long as it doesn't do it for sustained periods leading to thermal issues.
Even if the mechanical design was perfect and the chosen motor never went pass 100% FLA, the drive itself has efficiency losses.
Does anyone have any thoughts on this?
E: Is it just me or is the wording of 49.2 (and many other regs) leave things open for interpretation or differing opinions?
The equipment is coming from an international supplier and I'm not convinced they have calculated the panel nameplate FLA correctly, and before I put in a feeder servicing it I want to feel more comfortable.
My particular question revolves around motors that are controlled from a drive (VFD or Servo Amplifier) and whether or not to use the motor FLA or the drive's input current.
From searches on this board, it seems to be somewhat of a split opinion with regards to this for protection and feeder sizing, my concern is strictly regarding FLA calculation.
A) The supplier has provided an panel nameplate FLA that uses the servo motor FLA as a basis
B) The supplier has provided branch protection per the drive's current input values
I'm ok with B above, it's A that I have pause.
They contend that when the servo motor is detected by the servo drive that the drive automatically limits current, which in a base sense is true, except that I've personally been involved with servo applications where mechanical design wasn't great and given the dynamics of a servo, it's amplifier, it's tune, that a servo motor can easily be driven beyond it's nominal rating and in fact it's built to do just that so long as it doesn't do it for sustained periods leading to thermal issues.
Even if the mechanical design was perfect and the chosen motor never went pass 100% FLA, the drive itself has efficiency losses.
Does anyone have any thoughts on this?
E: Is it just me or is the wording of 49.2 (and many other regs) leave things open for interpretation or differing opinions?