In my searches I have found many answers that are not really answers.
In a multiple motor control panel using VFD's, do you use the VFD Input rating or the Motor FLA for calculating total FLA?
This panel is not my design but is a customers design.
Here are the "loads": (All are 460VAC 3-phase other than the CPT which is line to line on two of the legs)
VFD1=246A running a motor with 135 FLA
VFD2=106A running a motor with 45 FLA
VFD3=46A running a motor with 23 FLA
AC Unit=3.14 FLA
Control Power Transformer 3000VA @ 460VAC=6.52 FLA
UL508A states that in all calculations involving amperes, calculations resulting in fractions shall be rounded to the nearest whole number.
Is the "total FLA" of this panel 408FLA or 213FLA?
To me it makes sense to use the VFD Inputs because there is no guarantee to me that they will actually use the motor(s) that is(are) on the drawing or that they won't upsize the motor(s) at a future time if they discover that it(they) is(are) not strong enough for their application.
I would ask that you don't dance around the question with hypotheticals or irrelevant questions. This seems like simple math to me and there should really only be one answer unless there is a clear and concise description as to why it would need to be more complicated.
In a multiple motor control panel using VFD's, do you use the VFD Input rating or the Motor FLA for calculating total FLA?
This panel is not my design but is a customers design.
Here are the "loads": (All are 460VAC 3-phase other than the CPT which is line to line on two of the legs)
VFD1=246A running a motor with 135 FLA
VFD2=106A running a motor with 45 FLA
VFD3=46A running a motor with 23 FLA
AC Unit=3.14 FLA
Control Power Transformer 3000VA @ 460VAC=6.52 FLA
UL508A states that in all calculations involving amperes, calculations resulting in fractions shall be rounded to the nearest whole number.
Is the "total FLA" of this panel 408FLA or 213FLA?
To me it makes sense to use the VFD Inputs because there is no guarantee to me that they will actually use the motor(s) that is(are) on the drawing or that they won't upsize the motor(s) at a future time if they discover that it(they) is(are) not strong enough for their application.
I would ask that you don't dance around the question with hypotheticals or irrelevant questions. This seems like simple math to me and there should really only be one answer unless there is a clear and concise description as to why it would need to be more complicated.