DAB41162
Member
- Location
- Mason, OH.
- Occupation
- Electrical design and Controls Engineer
Hello,
I'm building an industrial control panel being fed by a 208V single phase source ( L1, L2, N, Gnd). It is part of an integrated measurement system that will need a UL label.
I know that UL508A says:
"66.5.3 The following color coding shall be used throughout the panel:
a) Black – all ungrounded power circuit conductors regardless of voltage;..."
However, NEC code says L1 be black and L2 be red. My thought is that a facility electrician would recognize the black and red wires, inside the panel, as power wires for L1/L2.
Thoughts?
I'm building an industrial control panel being fed by a 208V single phase source ( L1, L2, N, Gnd). It is part of an integrated measurement system that will need a UL label.
I know that UL508A says:
"66.5.3 The following color coding shall be used throughout the panel:
a) Black – all ungrounded power circuit conductors regardless of voltage;..."
However, NEC code says L1 be black and L2 be red. My thought is that a facility electrician would recognize the black and red wires, inside the panel, as power wires for L1/L2.
Thoughts?