Hi. this is my first time posting on this website. I am trying to get clarification on couple of different topics regarding the UL891 requirements 12th edition.
1. In order to certify a 480V switchboard to UL891, does the bolts that hold the bus bars and joints need to be SAE Grade 5 minimum? the only section in the UL891 that discusses Grade 5 bolt is under appendix G at the end of the document. There is not a whole lot of other explanation within the body of the document.
2. Table 23 covers the ampacity at the clamp joints. The rating ampacity of copper at the clamp joint is 200 amperes/in^2(up to 3000amps). let's say we have two
1/4x4 inch bus bar risers that are bolted together 90 degrees with two other runback bus bars with identical size. the question is when calculating the total surface area at the joint, the cross sectional area of the bar that are touching the adjacent bar on both side, do I added it up twice or only one time?
does anyone know of good reading material or reference books on bus bar sizing and calculation?
thank you
1. In order to certify a 480V switchboard to UL891, does the bolts that hold the bus bars and joints need to be SAE Grade 5 minimum? the only section in the UL891 that discusses Grade 5 bolt is under appendix G at the end of the document. There is not a whole lot of other explanation within the body of the document.
2. Table 23 covers the ampacity at the clamp joints. The rating ampacity of copper at the clamp joint is 200 amperes/in^2(up to 3000amps). let's say we have two
1/4x4 inch bus bar risers that are bolted together 90 degrees with two other runback bus bars with identical size. the question is when calculating the total surface area at the joint, the cross sectional area of the bar that are touching the adjacent bar on both side, do I added it up twice or only one time?
does anyone know of good reading material or reference books on bus bar sizing and calculation?