Bennie: The articles previously cited require that SE cable be installed in accordance with 338.30 which in turn requires that cable be "secured" every 4 1/2 feet maximum. This would rule out the installation of SE cable in a raceway longer than 4 1/2 feet, unless one could come up with a device that would secure the cable inside the raceway. On another note, UL does not list any SE cable for installation anywhere other than aboveground: Service Cable (TXKT) and Service Entrance Cable (TYLZ). This fact does not address your question, but does address the propriety of the installation described in the initial post. Personally, however, I would be mostly concerned about possible cable failure from excessive temperatures. As you are aware, the ampacity of conductors and cables is higher in free air than it is when installed in a raceway or embedded in insulation. I will attempt to contact a cable manufacturer, such as Southwire or Alcan, to learn their position on this matter. I will post that info when I have it. Thanks for your thoughtful inquiries.