Un-insulated Service Neutral

Status
Not open for further replies.

patricknola

Electrical contractor/Generac Dealer
Location
new orleans, La, United States
Occupation
Electrical contractor.
Hey Guys, I'm doing work in a neighborhood down here in New Orleans. I'm noticing an un-insulated neutral conductor being run by the local utility to the service mast. The home owner's all have a insulated neutral running up the service mast but where is splices to the utility drop, the utility ran an un-insulated conductor from the transformer. Is this an old practice or am i missing something? Help a brother out!
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The neutral can be uninsulated right up to the service disconnect even in a raceway down the side of the house.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That bare conductor is also connected to your meter base, electrodes, water piping, etc., so there's no touch hazard.
 