mbrooke Batteries Included Location United States Occupation Technician Feb 20, 2020 #1 What would an un-metered service look like since there is no need for a meter pan? Go directly into the panel, have a J-box or an outdoor main?
What would an un-metered service look like since there is no need for a meter pan? Go directly into the panel, have a J-box or an outdoor main?
mivey Senior Member Feb 20, 2020 #2 Picture, if you will, the meter box. Now imagine it is replaced with a piece of conduit. That about sums it up.
Picture, if you will, the meter box. Now imagine it is replaced with a piece of conduit. That about sums it up.
kwired Electron manager Location NE Nebraska Occupation EC Feb 20, 2020 #4 As far as what is on the building it is no different than if the metering is at the pole or other utility structure. Pad mount transformer with CT metering at the transformer - wiring goes directly to service disconnect(s).
As far as what is on the building it is no different than if the metering is at the pole or other utility structure. Pad mount transformer with CT metering at the transformer - wiring goes directly to service disconnect(s).