1.21 gigawatt
New User
- Location
- PA
- Occupation
- Time Traveler
Should we beat this dead horse a little more? There is a lot of discussion about parallel neutral paths and how sometimes it is unavoidable. Here's the current scenario that I'm struggling with.
This is new service to a mobile home disconnect. The utility requires the meter socket and disconnect to be mounted on RMC posts with strut channel supports. The grounding requirement is per NEC and simple enough. Utility also requires metallic conduit between meter socket and disconnect with bond bushings. All that is straightforward enough until you bond the ground and neutral in the disconnect like we're supposed to. There is now a parallel neutral path from that bonding point to the factory neutral/enclosure bond in the meter socket.
I can't see any way to eliminate this parallel path. One of the problems is that there are three different inspectors involved and they might disagree somehow. There has to be a solution to this NEC/Utility conflict.
Thoughts?
This is new service to a mobile home disconnect. The utility requires the meter socket and disconnect to be mounted on RMC posts with strut channel supports. The grounding requirement is per NEC and simple enough. Utility also requires metallic conduit between meter socket and disconnect with bond bushings. All that is straightforward enough until you bond the ground and neutral in the disconnect like we're supposed to. There is now a parallel neutral path from that bonding point to the factory neutral/enclosure bond in the meter socket.
I can't see any way to eliminate this parallel path. One of the problems is that there are three different inspectors involved and they might disagree somehow. There has to be a solution to this NEC/Utility conflict.
Thoughts?