Hello Everyone,
In a normal situation where we have a utility transformer (MV-Pri & 480Y/277V-Sec) and few step down transformers from (480 Delta- 208Y/120V). The unbalance load at 208Y/120V level will cause the unbalanced current to flow through the neutral back to the source (Star at transformer sec). My questions
1. Does the delta winding (primary side) of the 480-208Y/120V transformer sees unbalanced load similar to the secondary side? if so, how is this unbalanced load is handled at the primary side since there is no neutral?
2. If most the loads from the main service are transformers, 3-phase motors (balanced loads) and few lighting panels (277V circuits), does that mean the main service neutral conductor can be reduced to lets say half the size since not much 277V circuits used? My concern is just the unbalanced load coming from the step down transformers but if the unbalanced current is handled at the transformer secondary (208Y/120v level) then I will think there is not unbalanced current seen at the upstream utility transformer.
Any thoughts?
Thanks,
In a normal situation where we have a utility transformer (MV-Pri & 480Y/277V-Sec) and few step down transformers from (480 Delta- 208Y/120V). The unbalance load at 208Y/120V level will cause the unbalanced current to flow through the neutral back to the source (Star at transformer sec). My questions
1. Does the delta winding (primary side) of the 480-208Y/120V transformer sees unbalanced load similar to the secondary side? if so, how is this unbalanced load is handled at the primary side since there is no neutral?
2. If most the loads from the main service are transformers, 3-phase motors (balanced loads) and few lighting panels (277V circuits), does that mean the main service neutral conductor can be reduced to lets say half the size since not much 277V circuits used? My concern is just the unbalanced load coming from the step down transformers but if the unbalanced current is handled at the transformer secondary (208Y/120v level) then I will think there is not unbalanced current seen at the upstream utility transformer.
Any thoughts?
Thanks,