starsandstripes
Member
- Location
- SE Michigan
I have a new motor installation; 20 hp, 460v 3ph, nameplate 24 amps for a belt drive air handler. S.F 1.15. Two legs read 26 amps while running, but the third reads 21 amps. Loosening the belts did not drop the voltage and the driven shaft bearings are good. Voltage between all legs is around 478v; each leg to ground is 277v.
What are the causes for unbalanced amp readings and is this enough to cause overheating? I know it is under the service factor amps, but I still don't like it. Any comments would be welcome.
Thanks.
What are the causes for unbalanced amp readings and is this enough to cause overheating? I know it is under the service factor amps, but I still don't like it. Any comments would be welcome.
Thanks.