If you have Excel, download my calculator in the thread linked to earlier (let me know if the link does not work).Can anyone help with how to figure what the unbalanced current would be on a Wye system neutral?
For example:
Phase A is 130 amps
Phase B is 110 amps
Phase C is 90 amps
What would the amps be on the neutral.
What's wrong with 120 degrees for 3 phase? What else do you have?
Says who?And if their not 120 deg apart, then you have to use symmetrical components.
And if their not 120 deg apart, then you have to use symmetrical components.
Well, there is another way. You can use trigonometric identities and solve it long-hand.Says who?
Well, there is another way. You can use trigonometric identities and solve it long-hand.
The voltages are 120 degrees apart. The currents might not be.What's wrong with 120 degrees for 3 phase? What else do you have?