Unbalanced Current

Status
Not open for further replies.

EEC

Senior Member
Location
Maryland
If there is 40 amps of unbalanced current on the neutral. Can you read that current with clamp over amprobe. If so, back at transformer, where does the 40 amps go on Delta/pri-Wye grounded secondary?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
EEC said:
If there is 40 amps of unbalanced current on the neutral. Can you read that current with clamp over amprobe.

Yes

EEC said:
If so, back at transformer, where does the 40 amps go on Delta/pri-Wye grounded secondary?

For simplicity it goes back into the source being the windings/ transformer.

For example, (using single phase) to have any unbalanced current on the neutral the neutral conductor has to be common to more than one ungrounded (hot) conductor on opposing ends of the winding, see the following illustrations.

Unbalanced neutral

unbalanced__neutral.JPG


True Neutral

true_neutral.JPG


Kirschoffs current law says in effect that, current leaving the source must be equal to current returning to the source

Roger
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
080529-1900 EST

EEC:

Yes if 40 A is flowing in the Y neutral, then you can read it with a clamp-on current transformer or meter. The neutral being grounded has nothing to do with the question unless you have some other source of energy connected to the neutral besides the three Y secondaries.

So consider no grounding of the neutral. To get a neutral current there must be an unbalance of the current in the hot legs.

Also delta primary has nothing to do with the question that I believe you are asking.

.
 
EEC said:
If there is 40 amps of unbalanced current on the neutral. Can you read that current with clamp over amprobe.

Of course.

EEC said:
If so, back at transformer, where does the 40 amps go on Delta/pri-Wye grounded secondary?

It is called unballance(d) load when there are uneven loads between the phases. Ballanced currents flow between the phases and the unballance returns from the phase via the neutral.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
EEC said:
. . . where does the 40 amps go on Delta/pri-Wye grounded secondary?
Some of it flows into the Phase A secondary winding, and some into the Phase B, and the rest into the Phase C. And moment by moment, throughout the "60 times per second cycle," how much goes which way will change. But the simple truth is that with four wires (and no other stray paths) leaving the transformer, any current that leaves on one must necessarily return on one or more of the others. At all moments, the sum of the currents on the four wires must equal zero amps.
 

Lcdrwalker

Senior Member
Location
Columbus, Ohio
charlie b said:

Some of it flows into the Phase A secondary winding, and some into the Phase B, and the rest into the Phase C. And moment by moment, throughout the "60 times per second cycle," how much goes which way will change. But the simple truth is that with four wires (and no other stray paths) leaving the transformer, any current that leaves on one must necessarily return on one or more of the others. At all moments, the sum of the currents on the four wires must equal zero amps.
This is also true, through the windings to the primary side.
 

Smart $

Esteemed Member
Location
Ohio
charlie b said:

...At all moments, the sum of the [instantaneous] currents on the four wires must equal zero amps.
Hmm... more accurate and perhaps better understood as modified?

Sidenote: When using RMS current values, one must account for phase relationships to make the sums equal zero.
 

Smart $

Esteemed Member
Location
Ohio
weressl said:
Hmm...... could you explain to me what is the difference between 'all moments' and 'instantaneous'?
Hmm...

'At all moments' includes 'all' points in time, and as originally stated, the values do not have to be time correlated with one another. For example, the amount of current on Line A at 6 secs and Line B at 6.1 secs meets the criteria of 'at all moments'. Whereas 'the sum of instantaneous currents' restricts the values used to that of the same moment.

A couple ways to state it without inserting 'instantaneous' would be 'at each moment' or 'at any moment'.
 
Last edited:

Ranch

Senior Member
Location
Global
triplens?

triplens?

roger said:
to have any unbalanced current on the neutral the neutral conductor has to be common to more than one ungrounded (hot) conductor on opposing ends of the winding

Roger - might you want to consider triplens?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Thank you Smart, and you are correct, my answer does stand.

Ranch, there can be no additive current on one conductor of a two wire circuit, the current (including any distortion) would be the same through out (on both conductors) the circuit.

Roger
 

Ranch

Senior Member
Location
Global
To Smart and Roger,

I need to slow down, I surfed right by the fact this was a two wire circuit and I promise to read more carefully next time ....
 