I have two delta-delta transformers that have very unbalanced line to ground voltages on the secondary at no load. These are 480V-600V transformers.
AB: 614V A-Gnd: 560V 0 amps
BC: 610V B-Gnd: 505V 0 amps
AC: 610V C-Gnd: 104V 0 amps
I understand that line to ground to voltages can be unusual on a delta system, especially at no load. The issue I am having is that these unbalanced voltages are causing my ground fault relays to indicate a fault. I have verified that there are no actual ground faults.
I have the ground fault relays connected to shunt trip breakers. The idea is that if one of the legs goes to ground, the ground fault relay detects that and trips the breaker feeding the transformer primary. These relays are indicating a fault due to the voltage unbalance and trip the breaker as soon as the transformer is energized. If I disable the shunt trip and load up the transformer, the phase to ground voltages become much more balanced. The relay then no longer indicates a fault.
AB: 604V A-Gnd: 334V 490.9 amps
BC: 602V B-Gnd: 362V 492.1 amps
AC: 601V C-Gnd: 347V 489.2 amps
Has anybody ever encountered this before? If so, what are some solutions? These particular ground fault relays are Littelfuse EL3100. Maybe I need a different type of relay for this application or maybe I need to build something. One of my coworkers suggested the idea of perhaps getting a small delta-wye transformer, connecting the primary of that to the 600V source and connecting the secondary to the ground fault relay. The idea being that the wye secondary should be pretty balanced and then if there is a fault on one of the primary legs, the secondary voltage should go unbalanced enough to make the relays fault.
I appreciate any replies!
Thanks!
Thanks!