I have a 54kVA 3-ph transformer wired for 240V in a Y-config. No neutral wire to loads because all loads are 3-ph or single phase line-to-line.
Loads:
1x 240VAC 3ph with full load 19A (industrial chiller)
1x 240VAC 3ph 15A max input (5000W power supply with 0.95 power factor)
4x 240VAC 1ph 2000W power supplies (0.94 power factor)
4x 240VAC 1ph 650W power supplies (no power factor given - assumed 0.8)
For the 3 phase loads my kVA is:
240*19*1.73 = 7.898 kVA
and
240*15*1.73 = 6.325 kVA
Then I divide the 3 phase loads
For the single phase loads, I use the wattage and power factor to get kVA
2000/0.94 = 2.128 kVA
and
650/0.8 = 0.813 kVA
Because the single phase loads are line-to-line, do I then need to factor in 1.73? I'm pretty sure no, but I wanted to ask here.
From my understanding, I divide the kVA in half between the two phases they are connected to, so here is my load table:
Does this appear to be the correct method? Total load is 27.3 kVA?
Thanks
Loads:
1x 240VAC 3ph with full load 19A (industrial chiller)
1x 240VAC 3ph 15A max input (5000W power supply with 0.95 power factor)
4x 240VAC 1ph 2000W power supplies (0.94 power factor)
4x 240VAC 1ph 650W power supplies (no power factor given - assumed 0.8)
For the 3 phase loads my kVA is:
240*19*1.73 = 7.898 kVA
and
240*15*1.73 = 6.325 kVA
Then I divide the 3 phase loads
For the single phase loads, I use the wattage and power factor to get kVA
2000/0.94 = 2.128 kVA
and
650/0.8 = 0.813 kVA
Because the single phase loads are line-to-line, do I then need to factor in 1.73? I'm pretty sure no, but I wanted to ask here.
From my understanding, I divide the kVA in half between the two phases they are connected to, so here is my load table:
Voltage | Rated Amps | kVA | U | V | W | ||||
Chiller | 3Φ | 240VAC | 19A | 7.9 | 2.6 | 2.6 | 2.6 | ||
Power Supply | 3Φ | 240VAC | 15A | 6.2 | 2.1 | 2.1 | 2.1 | ||
Server Power Supply | 1Φ | 240VAC | 2.1 | 1.1 | 1.1 | ||||
Server Power Supply | 1Φ | 240VAC | 2.1 | 1.1 | 1.1 | ||||
Server Power Supply | 1Φ | 240VAC | 2.1 | 1.1 | 1.1 | ||||
Server Power Supply | 1Φ | 240VAC | 2.1 | 1.1 | 1.1 | ||||
Device Power Supply | 1Φ | 240VAC | 0.8 | 0.4 | 0.4 | ||||
Device Power Supply | 1Φ | 240VAC | 0.8 | 0.4 | 0.4 | ||||
Device Power Supply | 1Φ | 240VAC | 0.8 | 0.4 | 0.4 | ||||
Device Power Supply | 1Φ | 240VAC | 0.8 | 0.4 | 0.4 | ||||
Total kVA: | 8.7 | 9.1 | 8.0 | 25.7 |
Does this appear to be the correct method? Total load is 27.3 kVA?
Thanks