Hello, I am attempting to learn more about my worksite and the capacities of our systems. I have attained data but am having a hard time understanding exactly what is happening.
I am attempting to calculate efficiency of three seperate UPS Systems with real world data, one MGE, and two different Lieberts. The easiest way to acomplish this is to make an equation is to compare the kW in to the box to the kW out, or (kW IN)/(kW OUT)*100 = Percent efficiency
Data:
Module; Input A B C Voltage; Input A B C Amp; Output A B C Volts; Output A B C Amps; KW(displayed); KVA(displayed)
A1; 466, 469, 466; 259, 276, 260; 483, 480, 482; 168, 219, 183; 153; 157
A2; 468, 468, 467; 346, 361, 356; 482, 477, 480; 239, 282, 268; 215; 219
A3; 466, 468, 465; 299, 310, 294; 479, 481, 479; 225, 233, 187; 178; 178
B1; 474, 477, 473; 370, 318, 323; 486, 485, 487; 276, 309, 271; 235; 257
B2; 471, 474, 471; 373, 353, 361; 485, 485, 485; 311, 338, 314; 269; 282
B3; 473, 475, 474; 407, 390, 398; 480, 487, 491; 389, 352, 316; 295; 329
The forumula I was using to calculate Input Power was
(Phase A Power + Phase B Power + Phase C Power)/1.732 = 3 Phase Power
This was working somewhat reliable untill I discovered that unit B3 was displaying negative losses, or the input power was less than the output. So the formula isn't only wrong, but not even close. I also am confused about the difference between I (phase) and I (line). I am trying to find out what formula the UPS uses to calculate its power output, so I can do something similar to derive that power input by using an excel formula. Even if its complicated, excell will make it easy to calculate if I gather all the data.
Thanks in advace for your help.
I have attached a view of my spreadsheet for clarification.
http://img425.imageshack.us/my.php?image=untitledgj2.jpg
I am attempting to calculate efficiency of three seperate UPS Systems with real world data, one MGE, and two different Lieberts. The easiest way to acomplish this is to make an equation is to compare the kW in to the box to the kW out, or (kW IN)/(kW OUT)*100 = Percent efficiency
Data:
Module; Input A B C Voltage; Input A B C Amp; Output A B C Volts; Output A B C Amps; KW(displayed); KVA(displayed)
A1; 466, 469, 466; 259, 276, 260; 483, 480, 482; 168, 219, 183; 153; 157
A2; 468, 468, 467; 346, 361, 356; 482, 477, 480; 239, 282, 268; 215; 219
A3; 466, 468, 465; 299, 310, 294; 479, 481, 479; 225, 233, 187; 178; 178
B1; 474, 477, 473; 370, 318, 323; 486, 485, 487; 276, 309, 271; 235; 257
B2; 471, 474, 471; 373, 353, 361; 485, 485, 485; 311, 338, 314; 269; 282
B3; 473, 475, 474; 407, 390, 398; 480, 487, 491; 389, 352, 316; 295; 329
The forumula I was using to calculate Input Power was
(Phase A Power + Phase B Power + Phase C Power)/1.732 = 3 Phase Power
This was working somewhat reliable untill I discovered that unit B3 was displaying negative losses, or the input power was less than the output. So the formula isn't only wrong, but not even close. I also am confused about the difference between I (phase) and I (line). I am trying to find out what formula the UPS uses to calculate its power output, so I can do something similar to derive that power input by using an excel formula. Even if its complicated, excell will make it easy to calculate if I gather all the data.
Thanks in advace for your help.
I have attached a view of my spreadsheet for clarification.