Have storage type water heater 50 gal unbalanced with T1 at 41.6A and T2 and T3 at 24.0A all at 208V. So the question I have is if I take 41.6x1.25=52A then I get 60A as breaker size. However engineer provided 50A breaker??
Which would it be 50A or 60A?