408.13:Originally posted by shocku2: Also, where is this in the NEC?
Your panelboard is rated for 100 amps. The Article quoted above would require that you not load it beyond 100 amps. That is, if for example each of the loads was calculated to draw 40 amps, so that the total load was 120 amps, then the required feeder capacity for that calculated load would be a feeder with an ampacity of 120 amps. The panel would have to have a rating of at least 120 amps, and your 100 amp panel would not be acceptable.All panelboards shall have a rating not less than the minimum feeder capacity required for the load computed in accordance with Article 220.