Re: under counter low voltage lighting
This is a question that someone submitted to UL.
Is there Listed cable that is
permitted to be concealed
in walls for low voltage
lighting, other than NEC?
Chapter 3 cable?
Currently, UL does not List
standalone cable intended
for use in concealed locations
in accordance with the requirements
of Section 411-4 of the NEC?.
Section 411-4 of the NEC? requires
Chapter 3 wiring methods for concealed
wiring. Chapter 3 covers wiring
methods for all wiring installations,
unless modified by other
Articles in the code. Based on this reference
to other NEC? Articles, powerlimited
cable used in accordance with
Article 725 can be used for low
voltage lighting systems, provided
that the cable is supplied by a Listed
Class 2 or 3 transformer or power
supply. However, since most power
supplies provided with low-voltage
lighting systems are not Class 2 or 3,
Chapter 3 wiring methods are required,
unless the cable provided
with the Listed low-voltage lighting
system was evaluated for concealment
as part of the system?s Listing.
The proper cable would be specified
in the installation instructions provided
with the Listed system.
Paul