Hi
I designed a feeder-sets; (3) 3" pvc, (4) #500 MCM,cu in each based on ambient temp. , derating...
for a client who has 1200A service @120/208V, 3 ph.
And the local buildg & Safety approved the plan.!
Now, The inspector said " Change wires, they are down sized,
minu. 600 MCM required".
Any Comments, thoughts....????????
Thank you
Edward/ Toros