Under ground water pipe contiunity

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have underground metal water pipe as grounding electrode. It has water meter/filter device right where it enters little beyond 5 feet like 6 feet. I am required to provide bonding jumper per NEC 2014 section 250.53(D)(1).

I did research I would imagine this is equipment bonding jumper right at the service disconnect. However not sure. Would it be supply side bonding jumper.

Which table one uses to size the bonding jumper and where is it in code?
 
Last edited:
Yes supply side, 10 feet or more of underground water pipe "grounding electrode" NEC Table 250.66 ...If you're jumping the meter " bonding jumper" #6 cu
 
Yes supply side, 10 feet or more of underground water pipe "grounding electrode" 250.66 If you're jumping the meter " bonding jumper" #6 cu

Which table you used? Not sure how you got #6 cu. i have incoming service conductor 13 sets 500 kcmil Al into 4000A service disco.
 
Which table you used? Not sure how you got #6 cu. i have incoming service conductor 13 sets 500 kcmil Al into 4000A service disco.
That 6 is only for if you're jumping the meter .If you can get on the other side of it the then do so . I'll try to find it
 
Once you exceed 1750 kcmil in service conductors, the GEC is 3/0 Cu.. the "jumper" see post #6
 