75KVA step down transformer
480V to 120/208Wye
208FLA
X 1.25% =260A
next standard size breaker is 300A
I would like to make the secondary breaker 225, because that is a cheaper panel and main.
I do not expect inrush currents to be an issue and I can set the Instantaneous setting to 10X on the main.
is this a violation?
thank you for your time and have a good day