Hi,
Have a customer adding four 5-axis CNC machines to their facility. Nameplate on the equipment is 100A at 480V. They have existing spare 70A & 80A breakers that they are adamant they want us to use as the new 100A breakers are $600+ each. Conductors will be sized to the FLA of the nameplate.
From experience, we know that the machines never draw more than 40A as the parts the customer is in the business of making barely tax the machine (they already have a dozen of more).
I have no fear that the breakers will trip, or that there is any safety concern, but don't want to have a code violation. Worst case scenario is a nuisance trip (and possibly crashing a tool).
What specific code article would this be a violation of? Most everything motor related talks about sizing the conductors to the load and the OCP being sized to protect the conductor, not the possible FLA. I would like to be able to stand on a solid code reference should I refuse to do this.
Thanks.
Have a customer adding four 5-axis CNC machines to their facility. Nameplate on the equipment is 100A at 480V. They have existing spare 70A & 80A breakers that they are adamant they want us to use as the new 100A breakers are $600+ each. Conductors will be sized to the FLA of the nameplate.
From experience, we know that the machines never draw more than 40A as the parts the customer is in the business of making barely tax the machine (they already have a dozen of more).
I have no fear that the breakers will trip, or that there is any safety concern, but don't want to have a code violation. Worst case scenario is a nuisance trip (and possibly crashing a tool).
What specific code article would this be a violation of? Most everything motor related talks about sizing the conductors to the load and the OCP being sized to protect the conductor, not the possible FLA. I would like to be able to stand on a solid code reference should I refuse to do this.
Thanks.