Under Voltage Release or Shunt Trip

Status
Not open for further replies.

danilo

Member
Gentlemen,

For earth leakage protection,which between these devices are best used to trip the breaker?

Regards,
Danilo
 
I don't know if the application matters or not, but a UV trip can be a nuisance because it trips every time there is a power failure, requiring that you manually reset the breaker. Consider the implications of that.
 
I don't know if the application matters or not, but a UV trip can be a nuisance because it trips every time there is a power failure, requiring that you manually reset the breaker. Consider the implications of that.

Thanks Jraef, actually using UV is what i prefer for earth leakage protection to be on a "fail safe "mode but i worry about its coil because its always energized.
 
Gentlemen,

For earth leakage protection,which between these devices are best used to trip the breaker?

Regards,
Danilo

I have never seen a UV device used in a GF protection scheme. A shunt trip is used in this application if the GF relay is external to the breaker. If the GF protection is built into the breaker trip unit then a separate trip actuator trips the breaker.
A UV device is used to protect motor or other voltage sensitive loads by preventing single-phasing which can burn up the load. They normally have to be manually reset but I have seen cases where it is done remotely.
 
I have never seen a UV device used in a GF protection scheme. A shunt trip is used in this application if the GF relay is external to the breaker. If the GF protection is built into the breaker trip unit then a separate trip actuator trips the breaker.
A UV device is used to protect motor or other voltage sensitive loads by preventing single-phasing which can burn up the load. They normally have to be manually reset but I have seen cases where it is done remotely.

Hi Tony, yes it can be used in that protection scheme with an Earth Leakage Relay of course. A relay's NO contact is in series with UV coil.This contact closes when relay is energized and opens when de-energized or under fault condition,thus trips the CB.
 
Hi Tony, yes it can be used in that protection scheme with an Earth Leakage Relay of course. A relay's NO contact is in series with UV coil.This contact closes when relay is energized and opens when de-energized or under fault condition,thus trips the CB.

Danilo, I understand that it can work that way. :rolleyes: What I meant was that it was not the conventional way of wiring the circuit. ;)
 