underfloor raceways in industrial facility

Status
Not open for further replies.
visited a warehouse that has trenches built into the concrete floor with 1/2" steel cover plates as covers. A forklift managed to move a plate as it rolled over it and nailed a 480V conductor laying in the trench. Is this trench considered a raceway as other conduits run through here as well as other unprotected conductors feeding other equipment?

:?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
With the cover just laid in place rather than fastened, I would not call it a raceway. Certainly not a listed or approved raceway. More like a covered cable tray but not that either.
Probably not acceptable to put non- cable wire types there without a raceway.
Events prove it was not well protected against physical damage.
 

ADub

Senior Member
Location
Midwest
Occupation
Estimator/Project Manager
That's how our plant does things, we have trenches cut in the floor and then inset with steel. It is not a raceway. We use these trenches to get air, gas, power, welding grounds, and hydraulics from point A to point B. I wouldn't consider inside the trench susceptible to physical damage but we do it all in rigid regardless.


Sent from my iPhone using Tapatalk
 