Hello Every,
I'm working on a project (Data Center) which we are running 4000A feeders. typically we use 10 sets of 600Kcmil for this application and much more for derating. However, I'm using a software (Etap) to run the underground ampacity calculations. we will be using THWN2 conductor (90 deg) for this application but we will be using the 75 deg ampacity listed in the NEC since we are using 100% rated breakers. My question, as we all know, the THWN2 is rated for 90 deg but can I still choose the conductor temperature rise to be set at 90 deg since its rated for that or I need to set it for 75 deg since we using the 75 deg ampacity?
Anythoughts?
Thanks,
I'm working on a project (Data Center) which we are running 4000A feeders. typically we use 10 sets of 600Kcmil for this application and much more for derating. However, I'm using a software (Etap) to run the underground ampacity calculations. we will be using THWN2 conductor (90 deg) for this application but we will be using the 75 deg ampacity listed in the NEC since we are using 100% rated breakers. My question, as we all know, the THWN2 is rated for 90 deg but can I still choose the conductor temperature rise to be set at 90 deg since its rated for that or I need to set it for 75 deg since we using the 75 deg ampacity?