I don?t understand your use of the word ?derate.? What makes you think that the ampacity of the conductors might have been one value, but now must be given a lower rating because of something about the installation? If you put more than three current-carrying conductors in a conduit, then you reduce (derate) the ampacity of the conductors. If the ambient temperature is over 86F, then you reduce (derate) the ampacity of the conductors. Does one of these situations apply?
As to making selections of conductors and overcurrent settings, the process goes as follows:
? Step 1, calculate the load. You have done that, with the result of 2100 amps.
? Step 2, select a conductor that has an ampacity, under the installed conditions, of at least 2100 amps.
? Step 3, provide an overcurrent protection device that will protect the selected conductors.
So if you select conductors with an ampacity of only 2100 (e.g., 5 sets of 600 MCM THHN), then you must set the OCPD to no higher than 2100 amps. If you wish to use an OCPD setting of 3000 amps, then you must select conductors that have an ampacity of at least 3000 (e.g., 8 sets of 500 MCM THHN).