What is the maximum amount of turns that one can pull cable in conduit? And, is it against code to use pvc condulets as a pull point underground?
This, perhaps is a newbie question but, an engineer and I are having a "discussion" on maximum amount of degrees of bend in any one conduit run. Could you tell me which article deals with this issue? It's been my understanding for years that 360? is the maximum, even though ill advised it is to construct such a conduit run.Originally posted by tom baker:
360 degrees is the maximum, however, 270 is often more practical. it depends on what you are pulling. Keep in mind with PVC if the pulling tension is too high, you will burn through the elbows.
It would be difficult to use a condulet and maintain the required burial depth for PVC conduit.
You can pull through as many "turns" as you want, but code requires a pull point every 360 degrees of bend this can be any combination of degrees.Originally posted by klundy:
What is the maximum amount of turns that one can pull cable in conduit?
2002 NEC
358.26 Bends - Number in One Run. There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points, for example, conduit bodies and boxes.
Originally posted by klundy:
And, is it against code to use pvc condulets as a pull point underground?
2002 NEC
314.29 Boxes and Conduit Bodies to Be Accessible Boxes and Conduit Bodies shall, be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is used to establish the finished grade.
Exception: Listed boxes shall be permitted where covered by gravel, light aggregate, or noncohesive granulated soil if their location is effectively identified and accessible for excavation.